I'm plumbing a hot water boiler and am wondering if I can add on to an existing series loop with monoflow "T"'s to a seperate section. Will those 2 systems co-exist?

Thank you

Sibi
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
heat

NO. The MonoFlo will divert heat from the loop, and any units downstream will suffer. It could only be for a single radiator, not a zone, and the requirement for a MonoFlo system is that there has to be resistance between the two tees approximately equal to the resistance of the branch, which would be difficult to do in your installation.
 

sibi1972

New Member
Messages
32
Reaction score
0
Points
0
Wow.

Thank you for that answer. I was in HD today buying some copper and asked a guy there who said he knew about hydronics. He told me it would be fine.

I'm going to disregard what he told me, your answer makes sense to me and I'm not going to fool around with that series loop.

Sibi
 