View Full Version : Sewer transition, backflow & cleanout



rockosani
05-20-2005, 11:39 AM
I have a 4" cast sewer line and want to add a cleanout & backflow just outside where the line exits the house... about 3' underground. Can I remove a section and use PVC and, if so, what is the proper connector for the transition... a stainless steel clamp? I could never understand why a cleanout would be placed in the basement so that you would have to drain it there to get a snake into the line. My other thought was to put a riser in the basement and a 90 at the top to extend it outside, and forget the backflow, above the ground level... basement sill is about 2' above ground level. Any recommendations?

hj
05-20-2005, 08:42 PM
Install the cleanout outside and forget about the backflow valve.

rockosani
05-23-2005, 03:28 PM
Great... what's the proper transition piece to connect a PVC riser and cleanout to the older cast pipe?

hj
05-23-2005, 03:55 PM
In most areas a Mission/Fernco coupling