Severe Water Hammer from long downhill run.

Users who are viewing this thread

tobinator

New Member
Messages
11
Reaction score
0
Points
0
Location
Washington
Any advice? I have a 36" hydrant (quick close) and a 3/4" black poly line in approximately a 200' run with about 36' of elevation drop. In other words, my hydrant is WAY downhill from my home. When the hydrant is turned off, there is a HUGE shock wave that hammers the pipes in my house hard enough to damage something. My temp solution is to mostly close the supply valve that leaves my house, but that limits the volume too severly.

Directing a slow close is useless as I have three small kids.

I am thinking about a couple possible solutions:
* a spring loaded check valve near the hydrant
* a homestyle hammer arrestor- a tee with long 3/4" galvanized riser capped with a shrader valve to reintroduce air to cushion the hammer. The hammer arrestor would be inline with pipe run, not 90 degrees to it.

I want to do it right, NOT do it again.
Thanks,

Matt
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Why not a real hammer arrester? These have a piston and seal, and need no maintenance.
 