plenum rated pex tubing
isolatae
I need to run a 1/2" water line to feed a water cooler above a suspended ceiling in a comercial building. The ceiling is plenum rated. Do I have to use copper or is there a plenum rated pex available
I wondered the same thing, so I Googled it. Here's the what I found.
Plenums in buildings are enclosed spaces that are not for human occupancy, but are often used for heating, ventilating, and/or air-conditioning equipment and airflow, and for other equipment such as cables, piping, and luminaires. 'Plenum boxes' or sections are portions of HVAC air handlers or terminal units.
That doesn't really answer the original question, but at least Master Plumber Mark and I know what plenum means.
A plenum is often also an air duct, so a fire there can spread toxic combustion byproducts throughout the building. As a result, there are special rules about what can be put into them - they must not outgas poisonous compounds. No idea if pex does...but it should be in the materials data sheet.
If anybody's got a PEX MSDS handy, it might be mentioned in there. I see that UPONOR (manufacturer of WIRSBO PEX) sells a complete fire-suppression system, presumably plumbed with PEX, strongly implying it can be used in a plenum, but none of the PEX information sites I've visited mention plenum installation at all. I've sent a few inquiries off to manufacturers and the pexinfo site, but they've all knocked off for Sunday.
You can buy plenum-rated Cat. 5 phone/ethernet wire. Special jacket material. Costs about 4 times as much. Anxious to hear if there is a plenum-rated PEX.
There is no plenum rated pipe other than copper and cast iron that i know of. sorry...
and y'all are correct... a plenum (plenum rated stuff) is is the space above a ceiling and it is basically a huge return air duct. The idea is to not have anything that would give off toxic smoke when it burns. hth
Wirsbo PEX OK in a plenum... sort of
I just got a copy of Uponor's plenum rating to run from 0.50" to 2" PEX tubing within the plenum. You can't just throw it up there, unfortunately.
Oops. It's a 174KB .pdf file, too big to upload. If anybody would like a copy, I'll e-mail it to you.
The product description is "Cross-linked polyethylene tubing, identified as Insulated AquaPEX or hePEX, manufatured with a maximum outer diameter of 2" NPS, encased in fibreglass pipe insulation."
The tubing must be encased in fiberglass pipe insulation with a wall thickness of 1/2" to 1" and specific fire ratings. Insulated tubing runs shall be located at 0" minimum spacing for a maximum of 3 adjacent pipes with an additional 18" spacing to the next pipe run. There shall be no exposed tubing.
Practically speaking, it looks like Spiff's judgement is correct, although if you're willing to conform to the spec, you can run the PEX. You can probably run just about anything if you insulate it enough.
Plenum rated piping
For information - Plenum Rated specifically means that it meets ASTM E84 standard for Flame Spread Index of less than 25 and Smoke Developed values of less than 50. This doesn't mean that the substance won't burn, and it doesn't mean that the fumes aren't toxic, it just means that it spreads an gives off smoke within a certain rate.
If you have to use non-plenum rated materials in a return air plenum, you just need to cover it appropriately - you can meet code by wrapping the piping with insulation that meets the plenum rating (which most HVAC duct insulation does).
Basically check the HVAC system, if the air handler has 2 ducts coming out of it, and one of them is just open above the ceiling, that's called an open plenum return system and you have to meet the ESTM E84 requirements. If both the supply duct and the return duct go directly to grilles/diffusers then you are in the clear and there are no special requirements.
Much to my surprise, the Plastic Pipe & Fittings Assoc. (PPFA) have published information that BOTH PVC and ABS meet plenum rating requirements:
http://www.ppfahome.org/pvc/faqpvc.html
http://www.ppfahome.org/abs/faqabs.html
BUT, Charlotte Pipe (and every other resource i've ever seen on the subject) says that PVC and CPVC do NOT meet the requirements for plenum rating:
http://www.charlottepipe.com/Default.aspx?Page=ABSPVCDWV&type=ABSPVCDWV
I've been designing plumbing an HVAC systems for over 10 years, and I have avoided the use of any sort of plastic piping in plenum systems, but moreover, I avoid using open return plenum systems when ever possible - they have way more drawbacks than benefits, IMHO.
It's probably more info than you needed, but it's important to avoid getting turned down by a code official!