DWV Vent: Sanitory Tee at 45 Degrees

Users who are viewing this thread

Seaneys

New Member
Messages
192
Reaction score
0
Points
0
Location
Chicago Suburbs
I would like to make a few obvious improvements to my DWV before the inspector comes. I actually had goofed and put in a horizontal vent line in one place. The previous posts on this site made me aware of the error....

I would like to install a sanitary tee rolled 45 degrees as a vent off of a horizontal drain. The vent line rises vertically from a street 45 degree bend attached to the the sanitary tee.

Is this an advisable (code worthy) design? I've been trying avoid using sanitary tees (I find their use confusing), but I am tight on vertical clearance.

Thanks!
Steve

D:%5CDocuments%20and%20Settings%5Csseaney%5CDesktop%5CToilet_Vent.jpg
 

Attachments

  • Toilet_Vent.jpg
    Toilet_Vent.jpg
    44.6 KB · Views: 499
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
In Washington State, they would want a wye or combo fitting there.
In some cases, I would wye off, and then turn up through the floor with a waste 90 el, making sure the vent line would be above the flow line of the waste line.
 

Krow

Plumber
Messages
903
Reaction score
3
Points
16
Location
Ontario, Canada
In Canada, That layout is acceptable as long as you don't have anything draining into that branch. As long as its being used as a dry vent
 