crosby1
02-18-2008, 05:02 PM
Does a vent have to be a straight run or can it incorporate 90 degree right angles? I'm re-doing a shower stall; one wall is going to be glass block...right in the middle of that wall is a vent, so I'm wondering if I can simply re-route the vent to the other side of the stall using 90 degree connections and then up to the attic to meet up with the existing vent there?

thanks.

Herk
02-18-2008, 05:38 PM
Yes, a vent can have offsets in it. Codes have formulas regarding the distance the vent can travel horizontally. They also have requirements regarding the number of fixture units that can be handled by a particular size vent, though it's possible that neither of these would be factors in your case.

crosby1
02-18-2008, 05:46 PM
thanks herk.

basically all i want to do is re-route the vent from "A" to the other wall "B".

the vent is between the jacuzzi tub and the shower stall.

i'd run the new vent under the shower floor and up the wall marked "B" in the photo. then in the attic, back across to stack "A".

i hope this is clear.

thanks again.

pietre.

jimbo
02-18-2008, 08:46 PM
Not sure what your plan is, but the one big restriction is the vent CANNOT run horizontal ( less than 45º) until it it at least 42" higher than the floor.

crosby1
02-19-2008, 05:27 AM
thanks.

there's actually going to a knee-wall on the left to about 48". i think i'll run the new vent in that wall and then run it vertically up the back.

thanks for the suggestions.

p.