Order of vents - traps

entrinsic

New Member
Messages
2
Reaction score
0
Points
0
Location
Alberta
Form has been a great resource but can't find an answer to what may be a simple question.

I'm re-plumbing a basement bathroom and Utility room, running all drain lines below the slab (original not permitted and very sketchy).

From the main stack moving upstream the order of the fixtures /tie-ins are as follows: The main line to the sewer is 4" and the lien I intend to run starts as a 3:, ends a a 2".

Toilet - 3" into a wye into the 3" new line - within critical distance of the stack, no secondary vent

Lavatory - 2" to wye into 3" new line - seperate 1.5" vent line run in wall to main stack vent tie-in

Floor drain - 3" P-trap to 3" line to wye into 3" new line - no vent, within 12' of main stack as per my code/inspector (Alberta Canada) new line reduces from 3" to 2" upstream of the wye that ties in the floor drain

Shower - 2" p-trap to wye into 2" new line - vent is 1.5" line 2' upstream of shower tie-in wye (this is part of my question)

Clothes Washer / Lanundry Tub - 2" p-trap below grade into 2" line - vent is same vent as described for the shower, but washer/laundry tub p-trap is within critical distance of the 1.5" vent.

Diagram is attached.

My question, is there an issue with the washing machine/laundry tub and the shower sharing the vent where that vent is 3' downstream of the laundry p-trap and 2' upstream of the shower p-trap? Is the 2" line large enough to act as a wet vent for the shower for that 2' horizontal run?

Effectively the laundry vent is downstream of the lanudry p-trap while the shower vent is upstream of the shower p-trap.

Thanks,

Jeff
 
My question, is there an issue with the washing machine/laundry tub and the shower sharing the vent where that vent is 3' downstream of the laundry p-trap and 2' upstream of the shower p-trap? Is the 2" line large enough to act as a wet vent for the shower for that 2' horizontal run?

Effectively the laundry vent is downstream of the lanudry p-trap while the shower vent is upstream of the shower p-trap.

You can't wet vent those two fixtures together. The laundry needs to be connected independent of other fixtures.
 
You can't wet vent those two fixtures together. The laundry needs to be connected independent of other fixtures.

When you say "laundry need to be connected independant of other fixtures" do you mean only as applies to venting or as a completely seperate tie-in to the main line that doesn't have other fixtures draining into the line leading to the main drain?

Having trouble attaching the picture, the pdf is too large.

thanks,

Jeff
 
When you say "laundry need to be connected independant of other fixtures" do you mean only as applies to venting or as a completely seperate tie-in to the main line that doesn't have other fixtures draining into the line leading to the main drain?

Having trouble attaching the picture, the pdf is too large.

thanks,

Jeff

Yup you should have the Laundry tide into the main line independent of your other fixtures. Laundries discharge really fast. Laundries also discharge lint that causes clogs.

I use the Mass State code just so you know.
 