01-23-2008, 08:42 PM
Looking for input on my DWV for 3 lav's.
Planning on everything being 2 inch cpvc. Assume 1/4 slope for the horizontal drain.
Questions:
1. The 90 elbow will be in a stud wall. Will that work?
2. Do I even need the vent for the double lav?

3637

3638

3639

Thanks,
Amy

Redwood
01-23-2008, 08:47 PM
Close but no cigar! On the 2 closest to the verticle drop you have constructed an s-trap. Review your use of horizintal sani-tees.

Dunbar Plumbing
01-23-2008, 08:47 PM
The furthest fixture on the drawing is fine only if that vent is 42" up before it goes horizontal.


The two lavs need to be vented off tees, combined on the vents and go horizontal as one and on up. That involves 42" or higher as well.

jimbo
01-24-2008, 07:59 AM
All the vents must be 42" above the floor before they go horizontal.

The fixture drains must connect to the main with a wye and 45, not the santee shown.

orbea1
01-24-2008, 10:38 AM
Horizontal vents will be at least 42" above floor or 6" above flood level of the lav.

Is the 90 Ell in the wall going to be OK?
3647

3648

3649

cwhyu2
01-24-2008, 11:15 AM
Looks good to me.Eccept showervent should same hight as lav vent.

orbea1
01-24-2008, 11:30 AM
Thanks. That is actually a third lavatory. But I will make all the vents the same height.

cwhyu2
01-24-2008, 11:35 AM
Your welcome . thougt was a shower pipe it like the other two good to go.:)

ltnicks
01-24-2008, 05:22 PM
the 90's will work in this scenario, the drawings look good, only the numbers for pitch, height, minimum, and maximum are left out.:)

Lakee911
01-28-2008, 12:06 PM
I see some offset joints. Might get a clog there :)