View Full Version : Hot Water Supply Sizing



P-tank
03-20-2005, 10:56 AM
i'm looking to supply a 20 gal hw tank (laars endurance boiler) with 3/4" line for 2 floor 2 full bath unit. then i guess i'll run 3/4" line out too. but recently was wondering if i shouldn't go with 1/2" instead, thinking tap and shower might warm up quicker.

current connects to tank ar 1/2" but step up to 3/4" to enter the actual unit. i'm worried about adequate flow, etc. the hw part of this boiler has not been in use as of yet.

any thoughts and advice much appreciated

Gary Swart
03-20-2005, 11:14 AM
I think you have a valid concern about the time it takes to purge cold water from 3/4" lines, especially to the furthest fixture. I think 1/2" would be quite adaquate.

Terry
03-20-2005, 11:28 AM
Most plumbers are running at most 2 plumbing fixtures on a 1/2" line.

Tubs are rated at 4.0 fixture units, lavs at 1.0 for a combined total of 5.0
If you check the charts, you will see that 1/2" lines don't handle much more, maybe one more 1.0 lav.
Two bathroom groups, you should have 3/4" pipe.
http://terrylove.com/watersize.htm

http://www.iapmo.org/common/ROP2004/upc04rop/preprint/ch6.pdf

P-tank
03-20-2005, 12:18 PM
ok, thanks, i see this is a debated topic. i think i'll probably go with 3/4".