nelsonba said:
A few more questions...
2) Does the shower vent horizontal run have to be 42" above the floor or just 6" above the trap wier?
Thanks
Weir of the trap has no bearing on horizontal venting height, only on distance of trap to vent, offsets before vent and tailpiece length. But on to what you meant.
MN Plumbing Code:
http://www.revisor.leg.state.mn.us/bin/getpub.php?pubtype=RULE_CHAP&year=current&chapter=4715
4715.2540 VENT GRADES AND CONNECTIONS.
Subpart 1. Vent grade. All vent and branch vent pipes
shall be so graded and connected as to drain back to a soil or
waste pipe by gravity.
Subp. 2. Vertical rise. Where vent pipes connect to a
horizontal soil or waste pipe, the vent shall be taken off above
the center line of the pipe. The vent pipe shall rise
vertically, or at an angle not more than 45 degrees from the
vertical, to a point at least six inches above flood-level rim
of the fixture it is venting, before offsetting horizontally or
before connecting to the branch vent.
Subp. 3. Height above fixtures. A connection between a
vent pipe and a vent stack or stack-vent shall be made at least
six inches above the flood-level rim of the highest fixture
served by the vent. Horizontal vent pipes forming branch vents,
relief vents, or loop vents shall be at least six inches above
the flood-level rim of the highest fixture served.
STAT AUTH: MS s 326.37 to 326.45
Current as of 07/31/07
While it is legal to run the shower vent horizontally 6" above the spill line of the shower, your connection into the 3" vent stack must accomodate the same requirement of the water closet (as the 3" is it's vent).
Theoretically, it could be piped like this:
But, if one really wanted to be a devil's advocate, it could be argued that if all of the following occurred at once,
1: 3" stack below water closet plugged
2: water closet trapway plugged
3: shower trap plugged
water from the lavatory and toilet could compromise the horizontal potions of the shower vent, bringing with it paper and maybe some floaters (lol) that could stay after the stoppages were taken care of.
Now that is an extreme example that could probably only happen as a result of a fraternity prank, but it is possible. Just think if there was a waterproof partition that extended upwards from the lavatory!
Thats why we just pipe the stuff at 42", too much thinking otherwise.