Currently i have a monoflow system and is heating the basement and 1st floor. I would like to add a loop for the 2nd floor and make 2 zones. There is one circ pump and the supply and return are 1 1/4 copper. How do you suggest I add a 3/4 loop and create 2 zones?

Randy
 
Yes you can use 3/4 depending on how much water you will need. I would use a second pump, check valve and stuff. I would use 1†if it was me (you didn’t give much info).

You will need to make sure that your boiler will handle all of your heating loads.
 
You could also add a zone valve, but Got nailed has the better option, I prefer seperate circs for each zone.
If your asking if you could add a monoflo zone to the second floor from the first, I doubt it would work, far too much resistance for a monoflo loop to make it up a full story effectively.
 
I have a 500 and a 250 gallon wood boiler in series. I was using zone valves so I could cut down on the power usage. After the thought of if the pump burns out and I can’t get a new one for a few days and install it I’m sol. With one pump for each loop at least you will have some heat and be able to move the pump if you have to have the heat where you need it.

I now have 3 more pumps. One for a back up and still have not installed the other 2.

I will thank Grumpy for slapping me in to thinking about this.
 