On my boiler (Weil-McLain CGa5) , I have a temperature/pressure gauge on the supply side. There's no gauge on the return side. In the manual, it stresses that the return temp should not be less than 130 deg. How is this verified? Should there be a temp gauge on the return? Or does one calculate the theoretical return temp based on the BTU output of the baseboards?

The reason that I'm interested is to explore the possibility of having outdoor reset control installed on the boiler. In that case, it might be good to have a temp gauge on the return to monitor the temp.

hj
08-07-2007, 07:15 AM
It is not usually done, but you could just install a thermometer in the return line. If the temperature is too low, then you either have to large a system for the piping, or the flow rate is too slow and the water is losing too much temperature before it gets back to the boiler.

GrumpyPlumber
08-07-2007, 10:27 AM
Run the zones...put your hand on each one...if it's too hot to hold, your good, use common sense...don't grab it...touch lightly first.
130 degree's is the same as the max hot temperature of a faucets hot...barely able to put your hand under it.
The concern is if the temp gets too low from heat loss it could crack the CI exchanger...very unlikely unless you run hundreds of feet in extremely cold temps.