How many number 12 ga NM romex cables can enter one of the blue plastic single gang outlet/switch boxes? also is pig tailing outlets code?

jwelectric
07-23-2007, 09:08 AM
the number of conductors in a nonmetallic box is dependant on the cubic inch of the box.

Look at the inside back of the box and see how many cu. in. the box is.

brownizs
07-23-2007, 06:16 PM
Single gang outlet, you can go with three, four is just pushing it. Personally, I hate working on a job where it was not done right, and the wires are cut way too short (key point to remember).

jwelectric
07-23-2007, 07:47 PM
Most single gain non-metallic boxes come in 18, 20 and 22 cubit inches sizes.

314.16 is the section in the code that is used for box fill calculations. Here we are told that every conductor that enters the box counts as one conductor and all the grounds count as one conductor and the device counts as two conductors.

Using 12/2 with ground NM cable and a receptacle we would total all the conductors and multiply this by 2.25. Table 314.16(B) is where we get the multiplier from.

If there were two cables in one box then we would have a total of five conductors, two whites, two blacks and both grounds count as one. The device would be two more bringing our total to seven. 7 x 2.25 = 15.75

If we had three 12/2 with ground we would have a total of nine or 9 x 2.25 = 20.25.

This tell us that a 18 cu. In. box could be used if only two cables were installed but if three cables are installed then the larger 22 cu. In. box would be required.

brosnt1
07-24-2007, 08:04 AM
Thanks for the information, what about the pig tailing of recepticles and switches?

jwelectric
07-24-2007, 10:00 AM
Thanks for the information, what about the pig tailing of recepticles and switches?
They don't count for anything