View Full Version : Attic Bath Diagram
jasonmcl
02-08-2005, 11:41 AM
Could someone have a look and let me know what they think. Please ignore the bad art work. thanks
ssurell
02-21-2005, 10:18 AM
Wondering why you decieded to use 2" drain off the 1&1/2" lavatory and bath p-traps. I personally don't think it's worth the extra cost and hassle.
srdenny
02-21-2005, 10:26 AM
Clean outs at the end of the main line and the lavy branch would be nice. Also, your wc may not be to code (depends on which code is enforced in your area).
ssurell
02-21-2005, 10:37 AM
The other thing I see is: I would reduce the 3" to 2" vent at the Y fitting for the toilet. 2" fittings will fit in a standard stud wall where a special wet-wall or furred out wall has to be used for 3". Like I said in the previouse post, the cost of the fittings and pipe in addition to the added hassle of accomidating larger diameter pipe, I don't feel, is worth it when I don't see any advantage. Unless you're planning on sending large solids through, or you have to make a long run to get to your vent pipe, but then your p-trap has to be 2" also.
eddle6389
02-21-2005, 10:56 AM
I have a similar setup I am working on in my basement. Just curious..do you have to run a separate vent line for your tub even though you tub drain ties into you main vent stack and looks to be realtively close? If so - I guess I need to run a new vent line!!
Terry
02-21-2005, 11:45 AM
http://terrylove.com/images/dwv_b2.jpg
The toilet should be vented seperately from the other fixtures.
The revent should come in at 6" above the highest fixture, 42" is pretty safe for this.
You could use a 2x1.5x1.5x1.5 fixture fitting for the two lavs.
You can run one lav off 1.5" and when you combine them, it goes to 2".
The tub drain should be 2", in most cases you can use a 1.5" trap and trap arm.
srdenny
02-21-2005, 01:51 PM
Sure looks nice, Terry. If only the GC would give us 8" walls to fit it all into.
Terry
02-21-2005, 03:50 PM
8" would be nice.
The lower floor works with 6" and the upper with 4".
srdenny
02-24-2005, 06:40 PM
Terry
Unfortunately, in my area they enforce the UBC (section 2320.11.10) which only allows 2-3/16" maximum holes in 2x6 bearing studs and 3-5/16 maximum holes in 2x6 non bearing studs. Thus, I would not be able to drill the hole needed for the 3" which travels on a 45° to avoid the downstairs wc. However, I could run the second floor closet waste directly behind the downstairs wc and wet vent the upstairs lavy horizontally off the adjacent wc's 2" vertical vent (of course I would need a 2x6 wall upstairs to do it).
Terry
02-24-2005, 11:23 PM
In the drawing, I put the 3" line over so the drawing of the toilet wouldn't block it for learning purposes.
In the real world, I would have used a wye and street 45 and kept it within the 14.5" stud space behind the toilet.
In some cities here, we can wet vent the lav into the 2" wc vent, but not all cities.
Inspectors like to get their respect, sometimes by having their own interpretations of the codes.
One year I was plumbing in meat markets into food stores in ten cities.
After meeting with each inspector, I ran the plumbing ten different ways.
Every inspector thought he was the smartest in the state.
A little confusing though, running them that many different ways.
In Tacoma, one gold necklaced, open shirt to the chest inspector informed me that they didn't like outsiders doing "their" work.
I asked for the first inspector I had talked to and the inspection was completed.
I've always wondered if he was hinting for a bribe or if he was just goofy.
I remembered that my father used to tell me stories of Tacoma years ago, he was a district court judge in King county, and Pierce county used to bring him down there if they were "trying" one of their judges.
I hope things are better now there.
Anyway, it doesn't hurt to talk to your inspector before you get too carried away thinking you can just go by the code book.
srdenny
02-25-2005, 04:38 AM
Great story, Terry. Ten jurisdictionms, ten different interpretations. That's why my local plumber's assoc. has been holding quarterly code meetings for over 30 years. Get as many different code officials in one room at one time and talk code. Getting them all on the same page is money well spent. I also go to the local IAPMO meetings just to keep my ears to the rail and to show my interset in all things code. Knowing an inspector or his boss is invaluable. We rarely have any conflicts with inspectors and when we do, I research the problem and share my findings with the inspector. Occasionally, with officials like your gold chained guy from Tacoma, this is a waste of time. Mostly, it ends up being a nice introduction that often leads to professional friendship.
RioHyde
02-25-2005, 05:10 AM
Terry,
Glad to hear that we in Ohio arent the only ones in the nation that have to deal with umpteen interpretations of the code by different inspectors. Always a good idea to have a little pow-wow before doing anything for sure! The biggest problem we're facing IMO is that the code here only applies to 4 family and above residential dwellings and commercial buildings. When plumbing a single family home (or 2/3 family for that matter) we have to plumb it the way that particular jurisdiction wants it done whether its in the code book or not. Makes for some very confused plumbers at times. There is talk here of actually adopting a "residential code" though some are fighting it for various reasons. Making everything universal would be a good place to be, but I'm afraid every inspector will always interpret the code to his/her liking.
:confused: